tomofNV wrote:The 30A outlets I used to charge at RV parks 5-9 years ago in my converted car were 240V, verified by my energy meter which reads out AC voltage, current, power, and accumulated energy. I don't know much about RVs themselves.


Are you sure these were not 50 Amp outlets? Almost all RVs use TT-30 or NEMA_14-50.

https://en.wikipedia.org/wiki/NEMA_connector#NEMA_TT-30

Image

Three connectors: Hot, neutral and ground.

Most RVs are wired for 120V 30 Amp. Large RVs use 240V 50A.

https://en.wikipedia.org/wiki/NEMA_connector#NEMA_14

Image

Four connectors: Hot phase x, Hot phase y, neutral and ground.
#49 on the LEAF 100 mile club.
Most everything around here is wet during the rainy season. And the rainy season is long.
2012 Leaf SL Red
2014 Leaf SL Red
Can't sit in a Bolt seat, hoping for better soon.
Or perhaps a Buick version? Buick Electra 225???

SparkE
Moderator
Posts: 943
Joined: Sun Sep 11, 2016 5:53 am
Location: SF Bay Area

Re: Level 2 charger

Fri Sep 14, 2018 5:27 am

http://www.myrv.us/electric/Pg/30amp_Service.htm


30 Amp, 240V "Old Style" electric dryer plug, circa 1960s-1970s (NEMA 10-30) - 3 holes, one is an 'L' shape :

Image


30 Amp, 120V RV socket, (TT-30) - 3 holes, NO 'L' :
Note that you should never exceed 80% of 'rated' amps, so a max of 24 amp constant load on this one.

Image


50 Amp, 240V electric oven (and RV) socket, (NEMA 14-50) - 4 holes :

Image


And for the hell of it, 30A/240V "New Style" electric dryer socket, (NEMA 14-30) - 4 holes, one is an 'L' shape :
These are found in some garages. Note that you should never exceed 80% of 'rated' amps, so a max of 24 amp EVSE on this one.

Image

------------------------------------------ ------------------------------------------ ------------------------------------------

Image

tomofNV
Posts: 5
Joined: Thu Sep 13, 2018 5:31 pm

Re: Level 2 charger

Fri Sep 14, 2018 4:21 pm

I usually used a 50A site, NEMA 14-50, but a few times those were all taken so I used a 30A site, and it was 240 VAC. Maybe not common, dunno. Only used one at one RV park.